I disagree, David. It requires no such thing. It allows you to insert the 8KW into a calculation, and then compare the results to another approach to the load calculation, and allows you to use the lower result.
My answer to the original question is that you don't have to include anything at all for the gas range's electrical components. 210.52(B)(2), Exception 2 tells me that I can install a receptacle to serve the gas range's "supplemental equipment and lighting." Furthermore, I can put that receptacle on one of the small appliance branch circuits. Since those are already accounted for at 1500 VA each, regardless of whether any SABC has 2 or 3 or more receptacles, the receptacle for the range does not need to be counted separately.