Hey Guys,
I have this transformer setup at a solar installation which is basically used to convert 480/277V (Primary - To the Utility) to 208/120V (Secondary - From string inverters). There are 5 inverters (5 x 79.4 x 1.25) with 496.25A as the total maximum output current, and I used 3 sets of #3/0 (w/roof top temperature derate) to feed the transformer secondary.
Using inverters FLA (79.4 x 5 = 397A) & 480V, I calculated the transformer rating to be 330 KVA so I am using a 500 KVA transformer
Now the real question is should the transformer's primary conductors be sized by the name plate detail (500 KVA) or the transformers actual load (330 KVA)?
Because if I use the load, I am good with 4 set of #350 CU and 1200A primary OCPD. But if I go by the name plate, there is a significant increase the wire size and the OCPD which is 2000A.
Does NEC give details on this? I refered to 215, 450 and could not get a proper interpretation of the code. Any advice is much appreciated
I have this transformer setup at a solar installation which is basically used to convert 480/277V (Primary - To the Utility) to 208/120V (Secondary - From string inverters). There are 5 inverters (5 x 79.4 x 1.25) with 496.25A as the total maximum output current, and I used 3 sets of #3/0 (w/roof top temperature derate) to feed the transformer secondary.
Using inverters FLA (79.4 x 5 = 397A) & 480V, I calculated the transformer rating to be 330 KVA so I am using a 500 KVA transformer
Now the real question is should the transformer's primary conductors be sized by the name plate detail (500 KVA) or the transformers actual load (330 KVA)?
Because if I use the load, I am good with 4 set of #350 CU and 1200A primary OCPD. But if I go by the name plate, there is a significant increase the wire size and the OCPD which is 2000A.
Does NEC give details on this? I refered to 215, 450 and could not get a proper interpretation of the code. Any advice is much appreciated