hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Attached sketch I have main service breaker outside the building 30 feet away. From the outside main service breaker load side terminal you have four taps in conduit each going to disconnect inside building.
Each taps enter the building and go inside 90 feet to Disco #1, Disco #2, Disco #3, Disco #4 which have overcurrent protection as shown.
Four part questions:
1. Outside tap can be of ulimited length however I have taps done outside then going into the building 90 feet. Which tap rule outside, inside apply and should their be disco right when they enter?
2. Would outside feeder rule apply Nec 2014 Article 225.31 and 225.32 apply in this case?
3. Would POCO allow such install without trough and meter in the building but main service breaker outside?
4. Any other article that is non compliant with attached sketch?
I appreciate your input
Sent from my SM-G935U using Tapatalk
Each taps enter the building and go inside 90 feet to Disco #1, Disco #2, Disco #3, Disco #4 which have overcurrent protection as shown.
Four part questions:
1. Outside tap can be of ulimited length however I have taps done outside then going into the building 90 feet. Which tap rule outside, inside apply and should their be disco right when they enter?
2. Would outside feeder rule apply Nec 2014 Article 225.31 and 225.32 apply in this case?
3. Would POCO allow such install without trough and meter in the building but main service breaker outside?
4. Any other article that is non compliant with attached sketch?
I appreciate your input