Have a lighting inverter(has battery backup), fed from normal panel, feeding EM lights. Any code reason why you could run these circuits and the norm in same conduit?
 

tank728

Senior Member
Location
New Jersey
Occupation
Electrician
I don't think you can have line and load wiring this nature due to an article 700 violation of mixing normal power with an emergency source in the same raceway.
 

jap

Senior Member
Occupation
Electrician
I don't think you can have line and load wiring this nature due to an article 700 violation of mixing normal power with an emergency source in the same raceway.

And I would tend to agree with you.