General use receptacles on 30amp circuits

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

    #16
    Originally posted by mbrooke View Post
    You don't create one rule to prevent the violation of another- at least I believe that is the intent of the NEC.
    What does that mean ??

    JAP>

    Comment


      #17
      Originally posted by jap View Post
      What does that mean ??

      JAP>
      Meaning the code would not limit receptacles to 20amp circuits because someone might violate 240.4 (D)
      Our comedian shamelessly joked about a blackout. Talk about dark humor.

      Comment


        #18
        Originally posted by mbrooke View Post
        No, between several to two dozen 15/20 amp receptacles on a 30 amp circuit.
        Then my original answer stands.
        Master Electrician
        Electrical Contractor
        Richmond, VA

        Comment


          #19
          Originally posted by LarryFine View Post
          Then my original answer stands.
          Our comedian shamelessly joked about a blackout. Talk about dark humor.

          Comment


            #20
            Originally posted by mbrooke View Post
            I had said:
            Originally posted by LarryFine View Post
            My electrical theory is that 30a requires more metal in the current-carrying parts than 15/20a devices are made with, and OCPDs can't reliably protect the devices from overload damage.
            Master Electrician
            Electrical Contractor
            Richmond, VA

            Comment


              #21
              Originally posted by LarryFine View Post
              I had said:


              But are you going to see 4,400 to 4,600 watts of load on it? Doubt it.


              Ultimately 20amp OCPDs would be used, but the real world is different.
              Our comedian shamelessly joked about a blackout. Talk about dark humor.

              Comment


                #22
                Originally posted by mbrooke View Post
                But are you going to see 4,400 to 4,600 watts of load on it? Doubt it.
                To help us understand your thoughts a little better, why would the same not be able to be said about any device on any circuit?

                Why not ask: "Why shouldn't we be able to wire 15/20a receptacles on a 60a circuit?" What's different in your example?
                Master Electrician
                Electrical Contractor
                Richmond, VA

                Comment


                  #23
                  Originally posted by mbrooke View Post
                  But are you going to see 4,400 to 4,600 watts of load on it? Doubt it.


                  Ultimately 20amp OCPDs would be used, but the real world is different.
                  But, couldn't we apply that train of thought to most any Device/OCPD combination if we wanted too?

                  Why try and reinvent the wheel?


                  Jap>

                  Comment


                    #24
                    Originally posted by LarryFine View Post
                    To help us understand your thoughts a little better, why would the same not be able to be said about any device on any circuit?

                    Why not ask: "Why shouldn't we be able to wire 15/20a receptacles on a 60a circuit?" What's different in your example?
                    A short circuit might melt the plug to appliance flex cord before the breaker trips, if at all.
                    Our comedian shamelessly joked about a blackout. Talk about dark humor.

                    Comment


                      #25
                      Originally posted by jap View Post
                      But, couldn't we apply that train of thought to most any Device/OCPD combination if we wanted too?

                      Why try and reinvent the wheel?


                      Jap>
                      Unfortunately reinventing the wheel is the norm
                      Attached Files
                      Our comedian shamelessly joked about a blackout. Talk about dark humor.

                      Comment


                        #26
                        Originally posted by mbrooke View Post
                        A short circuit might melt the plug to appliance flex cord before the breaker trips, if at all.
                        Same with a lamp cord on a 30a circuit.
                        Master Electrician
                        Electrical Contractor
                        Richmond, VA

                        Comment


                          #27
                          Originally posted by LarryFine View Post
                          Same with a lamp cord on a 30a circuit.
                          But not for a 20?
                          Our comedian shamelessly joked about a blackout. Talk about dark humor.

                          Comment


                            #28
                            Originally posted by jap View Post
                            But, couldn't we apply that train of thought to most any Device/OCPD combination if we wanted too?

                            Why try and reinvent the wheel?


                            Jap>
                            Ignore "special purpose" its a office cubical receptacle
                            Attached Files
                            Our comedian shamelessly joked about a blackout. Talk about dark humor.

                            Comment


                              #29
                              Originally posted by mbrooke View Post
                              But not for a 20?
                              I'd rather see a #18 on a 20a breaker than on a 30a.
                              Master Electrician
                              Electrical Contractor
                              Richmond, VA

                              Comment


                                #30
                                Originally posted by mbrooke View Post
                                Ignore "special purpose" its a office cubical receptacle
                                Is this a question about the #10 neutral some partition wiring includes?

                                Or do you want to reduce the quantity of circuits to feed cubicle wiring?
                                Master Electrician
                                Electrical Contractor
                                Richmond, VA

                                Comment