Occ Sensor Control Wiring in same conduit with 277 volt lighting circuit?

Status
Not open for further replies.

Lbartowski

Member
Location
MN
I understand that if it's 0-10v dimming circuit, it's considered class 1, and needs to be separate from power conductors....but how about the "low voltage" control conductors going to an occupancy sensor?
 

Lbartowski

Member
Location
MN
Sorry....for clarification...I believe the 0-10v dimming conductors are considered class 2 circuits. My previous post said class 1.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The LV occupancy sensors that we install are Class 2 so their conductors cannot go in the same raceway as the power conductors. Some 0-10 volt lighting control can be reclassified as Class 1 and occupy the same raceway as the power conductors.
 

Johnhall30

Senior Member
Location
New Orleans, LA
Occupation
Engineer
You can put low voltage wiring in the same condiut as power conductors as long as the low voltage wiring is rated for 600V (i.e. you could use some #14 THHN)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You can put low voltage wiring in the same condiut as power conductors as long as the low voltage wiring is rated for 600V (i.e. you could use some #14 THHN)


That's a common misconception, Class 2 circuits that cannot be reclassified as Class 1 cannot be in the same raceway regardless of the voltage rating of the conductors.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
...unless it's in luminaire cable! I wonder how that is acceptable?
That is acceptable because of the separate jacket around the Class 2 conductors.
The argument is similar to the argument that two sets of wires, each inside their own EMT or Smurf tube, do not create a violation when those two raceways are run through a common enclosing raceway.

Sent from my XT1585 using Tapatalk
 

Lbartowski

Member
Location
MN
Right, but is luminaire cable really 2 separate raceways just because the control cable is jacketed? That logic would seem to allow me to pull a jacketed control cable (like an 18/3) within an EMT with 277 volt circuits then right?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Right, but is luminaire cable really 2 separate raceways just because the control cable is jacketed? That logic would seem to allow me to pull a jacketed control cable (like an 18/3) within an EMT with 277 volt circuits then right?
Right. If the control cable is a self-contained wiring method that does not require a raceway, it should be able to share the enclosing raceway. But without the explicit UL listing that luminaire cable has, an inspector may not agree.
 