I have (4)-20 amp double pole breakers feeding lights that doesn’t have a neutral. Can I use the 8 #12 current carrying conductors in a 3/4 conduit or do need to go to #10s to derate?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes derating is required because you have more than 3 CCC in a single raceway. Good news is that you can still use #12 AWG conductors.

#12 THHN = 30 amps @90 degrees C
30 amps*70% = 21 amps adjusted ampacity.

Welcome to the forum. :)
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
To follow Robs reasoning, depending on the insulation type of the conductors see article sections 110.14(C), 310.15(B)(3)(a), and 310.15(B)(16).

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, I did make some assumptions with the 90 degree C conductor. A 75 degree C conductor might also work if you can apply the next size up rule.
 