Breaker sizing derated wires

Status
Not open for further replies.

Hoodood

Member
Location
nyc
Occupation
Electrical foreman
We have this ongoing debate at work and get different answers. It concerns proper breaker rating for derated wires. I had an inspector tell me that if my #10wires were derated to 16amps I could not protect those wires with a 20amp CB. I said we were using the next size up rule since there are no 16amp breakers available. He said that if those circuits were to be put to where 18amps of load were being used then these wires would eventually heat up potentially creating a hazard. He made us change the 20amp CB's to 15amps and passed it. Is there anywhere in the code that states that you can not over protect a wire and you must use the next lower sized breaker?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
We have this ongoing debate at work and get different answers. It concerns proper breaker rating for derated wires. I had an inspector tell me that if my #10wires were derated to 16amps I could not protect those wires with a 20amp CB. I said we were using the next size up rule since there are no 16amp breakers available. He said that if those circuits were to be put to where 18amps of load were being used then these wires would eventually heat up potentially creating a hazard. He made us change the 20amp CB's to 15amps and passed it. Is there anywhere in the code that states that you can not over protect a wire and you must use the next lower sized breaker?

It depends on whether the conductors are part of a branch circuit supplying more than one receptacle...see 240.4(B)(1).

If yes, then no you can't use a 20A CB.

If no, then yes you can use the next size up as long as the load is 16A or less.
 

Hoodood

Member
Location
nyc
Occupation
Electrical foreman
Dedicated circuits only?

Dedicated circuits only?

Interesting! Nice. You've got me convinced as to why the inspector didnt allow this. Also I assume your talking about "single receptacle" dedicated circuits only.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Interesting! Nice. You've got me convinced as to why the inspector didnt allow this. Also I assume your talking about "single receptacle" dedicated circuits only.
See the section David mentioned in the 2011 NEC?

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Interesting! Nice. You've got me convinced as to why the inspector didnt allow this. Also I assume your talking about "single receptacle" dedicated circuits only.

You could use the next size up rule for more than single receptacle circuits. As David stated look at 240.4(B)(1). In your example was the load 18 amps?
 

Hoodood

Member
Location
nyc
Occupation
Electrical foreman
Thanks for the 240 reference. It should create quite the discussion tomorrow. A number of our foreman have been putting up to 40 CC's in 2 1/2" conduit. I have been installing only 20 in 1 1/2" conduit. They all say their's passes everytime using the next breaker size up rule. I always try to cover my bases especially after having to change out breakers before. I tell them it only takes 1 time and you never know when that will come! Thanks again!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thanks for the 240 reference. It should create quite the discussion tomorrow. A number of our foreman have been putting up to 40 CC's in 2 1/2" conduit. I have been installing only 20 in 1 1/2" conduit. They all say their's passes everytime using the next breaker size up rule. I always try to cover my bases especially after having to change out breakers before. I tell them it only takes 1 time and you never know when that will come! Thanks again!

What is the load on each circuit and what is it feeding?
 

Hoodood

Member
Location
nyc
Occupation
Electrical foreman
Thanks for the 240 reference. There is no known capacity rating since the circuits are of multiple duplex receptacles. So, 240.4 (B) (1) says no but 240.4(B) (3) says yes but 240.4 states ALL must be met. My assumption is that this circumstances does not meet code. It should create quite the discussion tomorrow. A number of our foreman have been putting up to 40 CC's in 2 1/2" conduit. I have been installing only 20 in 1 1/2" conduit. They all say their's passes everytime using the next breaker size up rule. I always try to cover my bases especially after having to change out breakers before. I tell them it only takes 1 time and you never know when that will come! Thanks again!
 

Hoodood

Member
Location
nyc
Occupation
Electrical foreman
Unknown capacity

Unknown capacity

As Ive stated it's a multiple Receptacle circuit so the capacity is unknown. That's why the inspector failed it to begin with. Although (B) (3) allows under 800amps to use the next highest size (B) (1) states multiple receptacles do not apply. So, seeing that not all the conditions under 240.4 have not been met I must use the lower sized breaker (15amps). One, on top of his game, inspector unlike those whom have let this pass!
 

Hoodood

Member
Location
nyc
Occupation
Electrical foreman
Doesn't apply?

Doesn't apply?

I'm reading that as if 2 different capacities apply. Such as temperature and conduit fill. When derating for only conduit fill then it is to my belief that your only applying 1 ampacity rating.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I'm reading that as if 2 different capacities apply. Such as temperature and conduit fill. When derating for only conduit fill then it is to my belief that your only applying 1 ampacity rating.

You can use the exception for derating also. Probably doesn't apply to your installation unless you're only talking about a small section in a long run of the raceway.

Since you have multi-receptacle circuits you cannot use the next size up rule. inspectors overlooking it does not make it code complaint.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Thanks for the 240 reference. It should create quite the discussion tomorrow. A number of our foreman have been putting up to 40 CC's in 2 1/2" conduit. I have been installing only 20 in 1 1/2" conduit. They all say their's passes everytime using the next breaker size up rule. I always try to cover my bases especially after having to change out breakers before. I tell them it only takes 1 time and you never know when that will come! Thanks again!

If you're only putting 20 CCC in the conduit then it should derate to 20A and the 20A breaker would be acceptable.
from the table, 10-20 conductors adjustment is 50%
50% of #10 @ 40A = 20A

This would be if you only had to adjust for the number of CCC and not temperature adj.
 