Table 310.15(B)(3)(a)

Status
Not open for further replies.

jbolen

Senior Member
I have some 1 1/2 EMT with 42 #12 xhhw current carrying conductors. What is maximum over current device for these circuits
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
10 amp overcurrent protective device if it is 90C. You need to increase the wire size and then reduce the number of conductors or use 2 runs of conduit
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
Is it going to make a difference with 42 ccc's?

To properly apply 310.15B16 one must first look at 310.104A.

In a dry location starting ampacity of #12 is 30 amps.
In a wet location starting ampacity of #12 is 25 amps.


I came up with 10 amps - dry / 5 amps wet.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
To properly apply 310.15B16 one must first look at 310.104A.

In a dry location starting ampacity of #12 is 30 amps.
In a wet location starting ampacity of #12 is 25 amps.


I came up with 10 amps - dry / 5 amps wet.

I think David's point is there probably isn't a 10 or 5 amp overcurrent protective device unless fuses are used. Not likely
 