Announcement

Collapse
No announcement yet.

Luminary cable without the MC

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

    #16
    Originally posted by hbiss View Post
    NO!

    -Hal
    Who are you responding to?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

    Comment


      #17
      Responding to Tortuga.

      He needs to read what GoldDigger said:

      Originally posted by GoldDigger View Post
      There is also an argument that if you put just the 16TFN twisted pair inside a jacket that would allow it to be used without a raceway as an NM family product, that can then be pulled into a raceway along with the individual THHN wires, making the result in conduit comparable in principle to luminary cable. But without a combined listing some (or most?) AHJs may not allow it.
      No doubt whatever in my mind that just pulling the combination into a raceway, regardless of how it was reeled, does not comply unless the control circuit can be (and is) reclassified to Class 1.
      If the reclassification can be done, then the bundle you would supply on one reel could be practical.
      -Hal

      Comment

      Working...
      X