TheElectrician

Senior Member
Hey Guys,

I already have the POCO defined transformer clearance in front of doors and windows and trying to figure out if NEC has a similar spec as I could not find it in NEC 450, it states only about ventilation and no specific clearance.

For example the POCO says the T/F should be 20' in front of the building and 10' in front of a window. Something like that. This is a 750kVA FR-3 Cooled T/F.

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The NEC has little to say about the installation of transformers in specific locations other than to follow the manufacturers instructions. Take a look at 450.9.
 