I agree to apply the NEC here we need to define the service point as defined in article 100.In addition,, keep in mind =your "240." Code reference may not the the most applicable.
Where is the service point ? If that is a POCO transformer (or customer) you may be dealing with Art 230 rules rather than Art 240.
Distance = 30 mIt would help to know distance and whether this is outside, inside or both. Does the MDP have a main????
It's Customer transformer not POCOIn addition,, keep in mind =your "240." Code reference may not the the most applicable.
Where is the service point ? If that is a POCO transformer (or customer) you may be dealing with Art 230 rules rather than Art 240.
Yes, i am in Egypt but i am dealing with project outside where NEC is followed.I agree to apply the NEC here we need to define the service point as defined in article 100.
And we need to know where the conductors are located, inside the building or outside etc.
m sleem Your in Egypt right?
Does the Ministry of Electricity recognize the NFPA 70 NEC as an acceptable standard? Have they amended it? (I would love to see a copy.) Or does you, your firm or your client just prefer to use the NEC?
And what version are you on?
I see your dealing with a three phase 50hz 13.5kV delta to 400Y230 system, such a system is not in the stock NEC yet.
With the 'minimum product standards' being deleted from the code and replaced with requiring more and more 'listed' equipment you probably will find it hard to implement the code as its intended, unless your using all North American products for some reason.
Where is it metered? On the primary side?It's Customer transformer not POCO
CoolYes, i am in Egypt but i am dealing with project outside where NEC is followed.
Per 240.21c, do we need an ocpd between tr and secondary conductors?
Where is "service point"? Customer may have to pay for the transformer even if it is on utility side of the service point, but doesn't necessarily mean they actually own it.It's Customer transformer not POCO
240.21(C) would require an OCPD within 7.5m secondary conductor length.
You may be able to use the 100m secondary conductor length per 240.92(C) if the installation is in a Supervised Industrial Installation.
Having ocpd between tr's secondary and conductors is not a common practice at least in our places, also conductors would be protected against short circuit by tr's primary ocpd, and it would be protected against overload by MDP main ocpd.240.21(C) would require an OCPD within 7.5m secondary conductor length.
Which is what happens with service conductors in otherwise NEC compliant applications, but you haven't made it clear exactly whether you are dealing with service conductors or secondary conductors of a separately derived system - per how NEC would apply.Having ocpd between tr's secondary and conductors is not a common practice at least in our places, also conductors would be protected against short circuit by tr's primary ocpd, and it would be protected against overload by MDP main ocpd.
yes, iam dealing with service conductors.Which is what happens with service conductors in otherwise NEC compliant applications, but you haven't made it clear exactly whether you are dealing with service conductors or secondary conductors of a separately derived system - per how NEC would apply.
240.21 doesn't apply to service conductors.yes, iam dealing with service conductors.
Having ocpd between tr's secondary and conductors is not a common practice at least in our places, also conductors would be protected against short circuit by tr's primary ocpd, and it would be protected against overload by MDP main ocpd.
Yes, you're right, i was just trying to know the reasoning behind if the cable is already protected as i mentioned in post #13You asked what the NEC required. What is common practice in your area is irrelevant if you are required to follow the NEC for this installation.
Per NEC services conductors are not considered to be protected. The service overcurrent protection does protect them from overload but will not protect against short circuits/ground faults that occur ahead of the service discconect. POCO may have overcurrent protection ahead of said conductors, it may very well allow much more fault current to flow before it trips than the service overcurrent protection would. Keep in mind Those service conductors are normally outside the building and don't pose as big of a threat if they overheat than if they are inside the building.Yes, you're right, i was just trying to know the reasoning behind if the cable is already protected as i mentioned in post #13
Yes, you're right, i was just trying to know the reasoning behind if the cable is already protected as i mentioned in post #13