    Originally posted by Dennis Alwon View Post
    I agree that 3/8" flex should be fine however if you read this (below) an inspector could turn it down. My personal opinion is where it says "where necessary" and inside the cabinet is not a place I would worry about
    Thank you Dennis

    Pulling 14/2 through 3/8 flex isn’t fun, but I’ve done it once before

    Leave a comment:


  • Kimura
    replied
    Originally posted by LarryFine View Post
    Using 14-2 MC will save you a lot of labor.

    May I presume 120v then?
    Im sorry, yes 120v

    Leave a comment:


  • Dennis Alwon
    replied
    BTW, will 14/2 even go inside 3/8" flex. We usually use 1/2" carflex and have never been turned down

    Leave a comment:


  • Dennis Alwon
    replied
    Originally posted by Kimura View Post
    My supervisor has asked me to spec a residential job for under cabinet lighting. I’ve located the power source from a lower floor. 1/2” EMT will pass up from lower floor, directly into lower part of kitchen cabinetry (into metal 4” JC)

    The other cabinet I need to get to is inaccessible via the basement , so I’m planning on running 3/8” flex up through lower cabinet and across cabinetry above microwave (to get to other cabinets)

    Per 334.15, flex should be sufficient for protection from physical damage. But getting conflicting answers.

    Thoughts?
    I agree that 3/8" flex should be fine however if you read this (below) an inspector could turn it down. My personal opinion is where it says "where necessary" and inside the cabinet is not a place I would worry about

    334.15(B) Protection from Physical Damage. Cable shall be protected
    from physical damage where necessary by rigid metal
    conduit, intermediate metal conduit, electrical metallic tubing,
    Schedule 80 PVC conduit, Type RTRC marked with the suffix -
    XW, or other approved means. Where passing through a floor,
    the cable shall be enclosed in rigid metal conduit, intermediate
    metal conduit, electrical metallic tubing, Schedule 80 PVC
    conduit, Type RTRC marked with the suffix -XW, or other
    approved means extending at least 150 mm (6 in.) above the
    floor.

    Leave a comment:


  • LarryFine
    replied
    Using 14-2 MC will save you a lot of labor.

    May I presume 120v then?

    Leave a comment:


  • Kimura
    replied
    Hi Larry. 14/2 inside

    Leave a comment:


  • LarryFine
    replied
    Are we talking 120v lighting or low-voltage?

    What are you considering putting in the 3/8"?

    Leave a comment:


  • Kimura
    started a topic 334.15 (Residential cabinets)

    334.15 (Residential cabinets)

    My supervisor has asked me to spec a residential job for under cabinet lighting. I’ve located the power source from a lower floor. 1/2” EMT will pass up from lower floor, directly into lower part of kitchen cabinetry (into metal 4” JC)

    The other cabinet I need to get to is inaccessible via the basement , so I’m planning on running 3/8” flex up through lower cabinet and across cabinetry above microwave (to get to other cabinets)

    Per 334.15, flex should be sufficient for protection from physical damage. But getting conflicting answers.

    Thoughts?