    #46
    Re: Outlets Per Breaker

    Somebody should probably mention that Charlie.

    The code minimum is sort of meant for convenience outlets where there aren't really any planned loads.
    Sam, San Francisco Bay Area

    Comment


      #47
      Re: Outlets Per Breaker

      Originally posted by physis:
      Yeeaahhh, my rriibbss are just about ready to meet there demise. MM,mmm, potatoes and gravy, phwew. I don't need you guys. I'll be juusstt fine

      Comment


        #48
        Re: Outlets Per Breaker

        Let's see if we can come to a conclusion pertaining to the number of receptacle outlets allowed on a branch circuit. There is NO limit for the number of recept outlets supplied by general purpose or small appliance branch circuits installed in DWELLING UNITS. For OTHER than dwelling units, the calculated load for receptacle outlets is 180 volt-amperes for each recept on a single yoke or strap.

        Comment


          #49
          Re: Outlets Per Breaker

          I haven't decided yet Dillon, but the Bar-B's loaded with mesquite. :cool:
          Sam, San Francisco Bay Area

          Comment


            #50
            Re: Outlets Per Breaker

            John,
            It may have taken 4 pages of posts but I think that you've summed it up very well.
            Rob

            Moderator

            All responses based on the 2017 NEC unless otherwise noted

            Comment


              #51
              Re: Outlets Per Breaker

              ok ok ok

              Someone look up in the code where if you run a 20 amp circuit and have one device attached. The device must be rated equal to atleast the overcurrent (breaker) rating.

              Now that's in the code. Here is states 1 outlet.

              Great discussion though.

              Comment


                #52
                Re: Outlets Per Breaker

                I'm not sure what your question is Bigjohn but I think the answer is in 210.23(A) through (D).

                Edit: left out an important word.

                [ May 04, 2005, 10:52 PM: Message edited by: physis ]
                Sam, San Francisco Bay Area

                Comment


                  #53
                  Re: Outlets Per Breaker

                  I see what your question is.

                  210.21.(B)(1) Single Receptacle on an Individual Branch Circuit. A single receceptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
                  Sam, San Francisco Bay Area

                  Comment


                    #54
                    Re: Outlets Per Breaker

                    Big john,

                    you said in your post:

                    a 20 amp circuit and have one device attached
                    this could be one 15 amp duplex receptacle. As Physis had stated only a single receptacle would be required to be rated for 20 amps. A 15 amp duplex would also satisfy this section.
                    Rob

                    Moderator

                    All responses based on the 2017 NEC unless otherwise noted

                    Comment


                      #55
                      Re: Outlets Per Breaker

                      Physis,

                      Other than dwellings 13 recpts. on a 20a circuit. That's why this Forum is so Great,I started in this trade in 1968 and never left it,and now in 2005 I just find out,13 recpts. on a 20a circuit.

                      frank
                      Frank Arizona,USA

                      Comment


                        #56
                        Re: Outlets Per Breaker

                        Frank, this forum is so definately indeed a great place.

                        I've brought up a recent situation where I somehow became responsible (I was never actually responsible) to sort of bring a commercial property occupant up to speed on his code compliance. I don't really do much commercial either.

                        I was rather amazed at how prepared and informed I was to deal with something like this. This web site and two books, one, the 2002 NEC, is my only source of knowledge.

                        This is most certaily a great place. :cool:
                        Sam, San Francisco Bay Area

                        Comment


                          #57
                          Re: Outlets Per Breaker

                          BigJohn67, Infinity:
                          210.21.(B)(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit. This means a single receptacle, NOT A DUPLEX recept.

                          Comment


                            #58
                            Re: Outlets Per Breaker

                            Physis,

                            The thing of it is all I do is comm/indst type work.There are blueprints for all the work,so it has never really been an issue.It's ironic that I never even heard the rule in all that time. Been fun talking with ya,later

                            frank
                            Frank Arizona,USA

                            Comment


                              #59
                              Re: Outlets Per Breaker

                              Well I challenge everything, give me a blue print, I hope it's right.
                              Sam, San Francisco Bay Area

                              Comment


                                #60
                                Re: Outlets Per Breaker

                                BigJohn67, Infinity:
                                210.21.(B)(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit. This means a single receptacle, NOT A DUPLEX recept.
                                That's exactly what I said. A post said a 20 amp circuit with one device. IMO one device means that it's on one yoke. A duplex is one device. If that device were a duplex receptacle than it could be a 15 amp duplex.

                                [ May 05, 2005, 11:47 PM: Message edited by: infinity ]
                                Rob

                                Moderator

                                All responses based on the 2017 NEC unless otherwise noted

                                Comment