    Motor load without neutral

    Can i supply 3 core cable without neutral to a 3 phase Y motor load? this is a client request,

    I think no as Per 250.24(C), am i correct?
    "Sleem"

    #2
    If the load does not need a neutral than you don't need to run one. That section you cited is for service equipment.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

    Comment


      #3
      Originally posted by m sleem View Post
      Can i supply 3 core cable without neutral to a 3 phase Y motor load? this is a client request,

      I think no as Per 250.24(C), am i correct?
      Motors do not require neutrals, they do require an Equipment Ground.



      Tom
      TBLO

      Comment