    Feed thru lugs

    Attached sketch shows xfmr feeding Panel R1-1 with 600kcmil phase conductors 400A main breker. Panel R1-1 is feed thru and feeds MLO 400A R1-2 via 600kcmil conductors. R1-2 has subfeed lugs which feed R1-3 with 200A main breaker via 600 kcmil conductors.

    Question is would 600kcmil conductors between Panel R1-1 and R1-2, Panel R1-2 a d R1-3 be protected by 400A main breaker Panel R1-1 or it depends on total demand load between panels?
    Attached Files
    Last edited by hhsting; 08-20-19, 08:45 PM.

    #2
    you have 400 amp protection on the feeders. You didn't state what size conductors supply the last panel, but everything is fine if they have an ampacity of 400 amps or even 351 amps for that matter. They also can have ampacity of 200 as long as lengths comply with feeder tap rules.
    I live for today, I'm just a day behind.

    Comment


      #3
      Looks OK but it's hard to say for certain because the handwriting is pretty poor.
      Rob

      Moderator

      All responses based on the 2017 NEC unless otherwise noted

      Comment


        #4
        Panel R1-2 has subfeed to last panel R1-3.

        The R1-3 is supplied by 4-600 kcmil + 1-3/0 Grd. R1-3 is 200A panel with main breaker of 200A.

        Comment


          #5
          Originally posted by hhsting View Post
          Panel R1-2 has subfeed to last panel R1-3.

          The R1-3 is supplied by 4-600 kcmil + 1-3/0 Grd. R1-3 is 200A panel with main breaker of 200A.
          Ah, so the conductors are all the same size, 600 kcmil. The 400 amp OCPD protects the 600's which are feed through at the second enclosure. The last panel has a 200 amp rating and a 200 amp main protected it. That 's all good. You could use a smaller SSBJ and EGC instead of the #3/0. The SSBJ minimum would be #1/0 and the EGC for 400 amps would be #3.
          Rob

          Moderator

          All responses based on the 2017 NEC unless otherwise noted

          Comment


            #6
            Originally posted by infinity View Post

            Ah, so the conductors are all the same size, 600 kcmil. The 400 amp OCPD protects the 600's which are feed through at the second enclosure. The last panel has a 200 amp rating and a 200 amp main protected it. That 's all good. You could use a smaller SSBJ and EGC instead of the #3/0. The SSBJ minimum would be #1/0 and the EGC for 400 amps would be #3.
            And as I said the last panel could be fed with 200 amp conductor - if length is short enough to comply with feeder tap rules
            I live for today, I'm just a day behind.

            Comment


              #7
              Originally posted by kwired View Post

              And as I said the last panel could be fed with 200 amp conductor - if length is short enough to comply with feeder tap rules
              He didn't mention length but given the conductor size he would be limited to 25'.
              Rob

              Moderator

              All responses based on the 2017 NEC unless otherwise noted

              Comment


                #8
                Originally posted by infinity View Post

                He didn't mention length but given the conductor size he would be limited to 25'.
                would work great on multi level building with panels on each floor that are right above the one below or if outdoors there is no length limitation for feeder tap.