We have been told that there is a required clearance of 24" to the side of an electrical enclosure that must be allowed for someone to stand while throwing a disconnect. ...
Nope. As S' said, 110.26.A .
Width of working space, as wide as the equipment, min 30" - for equipment ... "likely to require examination, adjustment, servicing, or maintenance while energized".
Non-fused disconnects (maintenance safety switch for example) often are not required to even have that. For example, HVAC motors tucked up in the overhead often have a disconnect switch right next to them and all you can see of the switch is the front. 110.26.A.4 Limited access is new this cycle, but doesn't change anything for non-fused safety switches.
That being said, all the electricians I've been around have been taught to stand to the side when opening current breaking contacts. Some will get pretty vocal if there isn't space to stand off to the side. If this is something that might be opened under
*significant load*, I agree.
Definition: *
significant load*:
A 3hp, 208V, 3ph, motor is not
A 100hp, 480V, 3ph is.
Everything in between - subject to interpretation;