Storage in allocated electrical area

Status
Not open for further replies.

JoeyO

New User
Location
Washington
Can anything be stored in a gated and locked area with two medium voltage transformers and disconnect gear. It is located in a parking garage under a hospital tower
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Yes, but only if the required working space and egress path(s) are maintained. I would be concerned, however, that allowing someone to store something will "open the gates" (sorry about that :roll: ) to others storing more things. This has a very real possibility of eventually blocking the working space or the egress path(s). There would be very real concern over how this is monitored and controlled.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I would be concerned, however, that allowing someone to store something will "open the gates" (sorry about that :roll: ) to others storing more things. This has a very real possibility of eventually blocking the working space or the egress path(s). There would be very real concern over how this is monitored and controlled.

But none of this is a code issue. You would have the same problem if it was a low voltage installation without a fence.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Oh I agree, Bob; no code issue here. But as professionals in the industry, we have the ability to express concerns and raise questions that lie outside code requirements. You yourself just posted a comment (with which I also agree) in another thread, suggesting that sometimes the best answer to a question is a question in the form of, "Why would anyone do that?" So in that vein, I am essentially asking why anyone would want to store things in the area mentioned.
 

PaulMmn

Senior Member
Location
Union, KY, USA
Occupation
EIT - Engineer in Training, Lafayette College
They want to use the existing 'storage area' rather than paying to fence in another area for storage.
 

tom baker

First Chief Moderator
Staff member
I had a same problem at maintenance facility. Our manager was an electrician so he knew exactly the clearance requirements. They started with a file cabinet, then used lamps and on and on. Eventually we got a new risk manager, the facility manager retired, so I sent a picture of the storage area and a graphic from Mike Holts materials. The next day everything was cleaned out thats the way its stayed. So perhaps get your safety department involved.
 