Prim and sec xfrmr

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Is there a code that states the maximum distance a panel can be on the primary or secondary side of a transformer? Ty

Sent from my SM-N960U using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A panel no but on the secondary there is a rule regarding the maximum conductor length from the transformer to the OCPD. Typically it's 25' for standard 3Ø, 480/208-120 transformers.
 