Overcurrent protection

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have manufacturer datasheet for kitchen equipment which requires Nema 15P receptacle with full load of 10 amps.

However duplex Nema 20R receptacle is provided with 20amp overcurrent with 2#12 and 1#12gnd.

Would I need 15 amp overcurrent protection or 20 amp overcurrent protection would be fine?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Table 210.21(B)(3) seems to state if the receptacle is 20 amp then a 20 amp overcurrent protective device is needed. I don't believe it will be an issue on a 20 amp circuit. We do that all the time with refrigerators that draw 7-8 amps on 20 amp circuits.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Unless the manufacturers instructions say that you need to limit the OCPD to 15 amps a 20 amp circuit is fine. As Dennis stated if you have a 20 duplex it must be on a 20 amp circuit.
 