    Custom receptacle strip under counter - listing?

    NEC 2014
    Faced with an application where a custom receptacle strip is needed under a counter. Permanent installation with ch3 wiring method. In an ideal world the fabricator could place receptacle cutouts in the right places in the frame of this thing (which is fully enclosed 14ga steel), the receptacles could be installed from behind, and conduit could enter from one end. But that would be a raceway that needs to be listed right? Looking for a workaround, off the shelf wiremold type products dont work for the application. Does a cover need to be listed? If the receptacles were installed in boxes behind the face with the receptacles protruding through their cutouts, then the face of this frame would become a cover plate.....

    I appreciate any suggestions

    #2
    Some months ago, I posted a photo of the SABC receptacles that were installed during a kitchen remodel that was finished last February. I looked, but have not yet found a copy of that photo at my work location. There are five sections of triangular-shaped metal enclosures, about 2 inches on a side, with the outlets on the "hypotenuse" side and the other two sides installed against the underside of the cabinet and against the back wall. All wiring is internal to the enclosure. The length of each section varies with its location (i.e., left and right of sink, left and right of range, and bar area). All kitchen walls had the drywall removed, and the electrician hard wired the outlets using Romex (I think that is the right term). I don't know if this helps. If I find that other thread, I will post a link. I believe I included the make and model of the outlet strips.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

    Comment


      #3
      Having a real hard time picturing your situation. A picture or at least a drawing would be nice.

      Is this commercial or residential?

      -Hal

      Comment


        #4
        Search for >computer rack vertical power strip<. These are multi-outlet strips intended to mount in a computer equipment rack, usually along the back rails. All of the 'stuff' in the rack plugs into the strip.

        Many (most?) are cord-connected. Many have the cord coming out the 'front,' where the outlets are, some have the cord coming out the end, fewer have cords out the back. I don't remember seeing any hard-wired models.

        https://www.cableorganizer.com/p/min...wer-extension/ <-- these are boxy duplex outlets, designed to be mounted under a desk. They have a hard-wired version...

        Click image for larger version

Name:	Minitap Hardwired.JPG
Views:	141
Size:	58.9 KB
ID:	2540349
        Last edited by PaulMmn; 10-18-19, 02:25 PM.

        Comment


          #5
          Here is the product I tried to describe. It is UL listed.
          https://www.hardwareresources.com/li.../TR18-2WD-P-WT

          Charles E. Beck, P.E., Seattle
          Comments based on 2017 NEC unless otherwise noted.

          Comment


            #6
            Originally posted by Todd0x1 View Post
            NEC 2014
            Faced with an application where a custom receptacle strip is needed under a counter. Permanent installation with ch3 wiring method. In an ideal world the fabricator could place receptacle cutouts in the right places in the frame of this thing (which is fully enclosed 14ga steel), the receptacles could be installed from behind, and conduit could enter from one end. But that would be a raceway that needs to be listed right? Looking for a workaround, off the shelf wiremold type products dont work for the application. Does a cover need to be listed? If the receptacles were installed in boxes behind the face with the receptacles protruding through their cutouts, then the face of this frame would become a cover plate.....

            I appreciate any suggestions
            Cant they just weld metal boxes behind the receptacle cutout? They could be interconnected with a raceway like FMC. This is how commercial kitchen equipment is set up. Don't ask me how they got this listed with the number of conductors in the boxes.
            Attached Files
            Rob

            Moderator

            All responses based on the 2017 NEC unless otherwise noted

            Comment


              #7
              You can use an enclosed channel as a raceway, like is done with store-front window framing.
              Master Electrician
              Electrical Contractor
              Richmond, VA

              Comment


                #8
                Thank you everyone for the product suggestions. Unfortunately this project does not lend itself to an off the shelf solution, the spacing between devices varies and has to be exact and the cover along its length has to be seamless (and the width is odd and has to be precise to match its mounting surface).

                Originally posted by LarryFine View Post
                You can use an enclosed channel as a raceway, like is done with store-front window framing.
                Can devices be mounted in such an enclosed channel, or would it then have to be listed?

                Comment


                  #9
                  Originally posted by Todd0x1 View Post
                  Can devices be mounted in such an enclosed channel, or would it then have to be listed?
                  Not sure about that. If the receptacles will have standard plates, you could use old-work boxes.
                  Master Electrician
                  Electrical Contractor
                  Richmond, VA

                  Comment


                    #10
                    Can you install listed boxes behind the custom channel and connect them with a listed raceway or cable? If so then you don't need to worry about the channel.
                    Rob

                    Moderator

                    All responses based on the 2017 NEC unless otherwise noted

                    Comment


                      #11
                      Originally posted by Todd0x1 View Post
                      Thank you everyone for the product suggestions. Unfortunately this project does not lend itself to an off the shelf solution, the spacing between devices varies and has to be exact and the cover along its length has to be seamless (and the width is odd and has to be precise to match its mounting surface).



                      Can devices be mounted in such an enclosed channel, or would it then have to be listed?
                      AGAIN! Pictures or we have no idea what you are talking about!

                      -Hal

                      Comment


                        #12
                        Originally posted by infinity View Post
                        Can you install listed boxes behind the custom channel and connect them with a listed raceway or cable? If so then you don't need to worry about the channel.
                        Yes, that was the plan B which is why I was asking if covers have to be listed

                        Comment


                          #13
                          Originally posted by hbiss View Post

                          AGAIN! Pictures or we have no idea what you are talking about!

                          -Hal
                          I haven't had a chance to draw anything up I will try to do so over the weekend.

                          Comment


                            #14
                            Originally posted by Todd0x1 View Post

                            Yes, that was the plan B which is why I was asking if covers have to be listed
                            They do not because you're installing the receptacles in listed metal boxes with a listed wiring method. Now if you want to pull individual conductors in the custom channel then it's being used as a raceway and a listing would be required.
                            Rob

                            Moderator

                            All responses based on the 2017 NEC unless otherwise noted

                            Comment