    Neutral Required for New Service?

    As the title says, would a neutral be required for a new residential service containing only straight 240v loads? This would be for off peak loads or PV where the inverters don't need a neutral. If yes can someone direct me to the code section?

    #2
    250.24(C)

    Roger
    Moderator

    Comment


      #3
      Neutral only to main, EGC only to load.
      Master Electrician
      Electrical Contractor
      Richmond, VA

      Comment


        #4
        Here is how I explain it in my classes.
        On the load side of the service there is a white wire and green wire. On the line side of the service, the white wire has an imaginary green stripe (since they are connected by the SBJ) If there is a line to case fault, the service neutral returns the current to the source (transformer), and back to the OCPD, which should open. With out a neutral, the line to case fault won't clear.
        Moderator-Washington State
        Ancora Imparo

        Comment


          #5
          Thanks y'all!