FM 200 and fire alarm

Status
Not open for further replies.

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Is it required to put fire alarm smoke detector aong with Fm200 detectors in critical areas, in light of NFPA?

You do not need general building smoke detectors in addition to those used to activate the FM200 inside the FM200 protected space. You do need to send the alarm signal from the FM200 panel to the main panel so the building notification appliances can be activated.
 