xptpcrewx
Power System Engineer
- Location
- Las Vegas, Nevada, USA
- Occupation
- Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
In what case would 215.2(A)(1)(b) ever be greater than 215.2(A)(1)(a)?
In what case would 215.2(A)(1)(b) ever be greater than 215.2(A)(1)(a)?
Thanks David. I would like to get some clarification on a few things:
1. Where does it say, or is it implied, that you may divide the maximum load current by the correction and/or adjustment factors to obtain minimum allowable ampacity? My interpretation is that the adjustment and correction factors are intended to be applied to the respective table ampacities in Article 310.
2. Couldn't "maximum load to be served" also include overload conditions?
David,
I understand your logic however there is something bothering me about the exact code language that doesn't seem to agree.
For example, there are two separate concepts at play:
1. "Minimum Feeder Size" (in terms of ampacity) which is the larger of 215.3(A)(1) or (b); and
2. "Conductor Ampacity " (for a given wire size) which is the smaller of the limiting temperature ampacity or the adjusted/corrected table ampacity.
For the feeder to be sized correctly, you would need to compare two ampacities; ampacity 2 would have to be greater than or equal to ampacity 1.
What are your thoughts. Thanks in advance.
David,
The point I am trying to make is that there are two different concepts here. It may be easier demonstrated if you answer the following questions with reference to your example:
1. What is the minimum required feeder size current?
2. For the wire size determined in 1., what is the ampacity?
These are not always the same value. Lets start there. Thanks
Ok. According to your example, the minimum feeder conductor size would have to have an ampacity of not less than 138A.
Now if you apply the rules of Article 310, then you will see #1 AWG (90*C) can only carry 116A under the conditions of use. Clearly you cannot use #1 AWG because it does not have the capacity.
So to re-emphasize:
1. The minimum required feeder size current = 138A
215.2(A)(1)(b) says the conductor shall have an ampacity of not less than the load to be served after the application of any adjustment or correction factor.
David,
I think we are getting somewhere, but 215.2(A)(1)(b) does not exactly say this:
215.2(A)(1)(b) - The minimum feeder conductor size shall have an allowable ampacity not less than the maximum load to be served after the application of any adjustment or correction factors.
So does "allowable ampacity" mean "table ampacity"?
I just checked the NFPA website, my handbook and a digital pdf copy... They all say "allowable ampacity". I am referencing NEC 2017.
The minimum required feeder size current is 110A, not 138A. The load is 110A, the conductor has to be able to carry 110A. Ampacity of conductor under consideration (1 AWG, 90*C) = 116A, which is greater than 110A.
I am familiar with 2011, and in my opinion that is very confusing as well. It would be much easier if they just eliminate the language and use equations instead.
Now that we have confirmed that 2017 language is broken, lets discuss intent.
What is the point of 215.2(A)(1)(b)? This seems redundant because of the rules in Article 310 already require that conductors not operate beyond their modified ampacity.
Suppose the minimum required feeder size current is 110A as you mentioned; again, in what case would this value ever be larger than 215.2(A)(1)(a)?
I am not sure why you think I am mixing concepts about cross-sectional area and ampacity. I am trying to limit this discussion to ampacity only.You're mixing concepts here. The SIZE (cross sectional area) of the conductor, and the AMPACITY of the conductor are different things.
The intent of the two sections (a) and (b) in 2014 and later Codes are still the same intent that I listed as (1) and (2) above from the 2011 Code.
Both 215.2(A)(1)(a) and (b) talk about "minimum feeder conductor size." So whichever section requires the larger "minimum size" prevails.
I suppose what is most broken about the current wording is the part of 215.2(A)(1) which says "Conductors shall be sized to carry not less than the larger of 215.2(A)(1)(a) or (b)." 215.2(A)(1)(a) and (b) already specify a conductor size, so 'Conductors shall be sized to carry not less than the larger size' doesn't really make sense.