Sizing ground conductor for fire pump

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
If using a 208/480V step up transformer, can you adjust the ground conductor based on what the secondary OCPD would have been? If not, you would have to size the ground conductor on the secondary based on the primary OCPD right?

For instance, a 1600A OCPD on the primary would require a #4/0 ground. For the secondary, a 600A OCPD would allow #1 ground (although secondary OCPD not allowed for fire pumps) but can you size the secondary ground conductor based on this 600A OCPD or do you have go off of the 1600A OCPD?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If using a 208/480V step up transformer, can you adjust the ground conductor based on what the secondary OCPD would have been? If not, you would have to size the ground conductor on the secondary based on the primary OCPD right?

For instance, a 1600A OCPD on the primary would require a #4/0 ground. For the secondary, a 600A OCPD would allow #1 ground (although secondary OCPD not allowed for fire pumps) but can you size the secondary ground conductor based on this 600A OCPD or do you have go off of the 1600A OCPD?

Interesting question, so you have a step-up transformer feeding the fire pump controller with no secondary OCPD and you're looking to size the EGC?
 

cppoly

Senior Member
Location
New York
Yup, correct! Secondary OCPD not allowed as per article 695.5. But we always size EGC as per the OCPD, but if OCPD is not allowed on secondary, you would have a way oversized EGC based on the primary OCPD.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Yup, correct! Secondary OCPD not allowed as per article 695.5. But we always size EGC as per the OCPD, but if OCPD is not allowed on secondary, you would have a way oversized EGC based on the primary OCPD.

I don't believe that you would have an EGC on the secondary, at least until you reach the Fire Pump Controller. I think it would be a supply side bonding jumper per 250.30(A)(2). Perhaps someone with more experience with that type of installation will chime in.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I agree with David. From the secondary terminals of a transformer to the first overcurrent device (in this instance, it is at the FP controller), you have an SSBJ. For a 600 amp service I would use (2) sets of 350 KCMIL copper conductors. Per Table 250.102(C), that would call for a 2/0 SSBJ.
 