Water pipe grounding

Status
Not open for further replies.

Eagle126

Member
this job is in Massachusetts, residential home, upgrading a service to a 200 amp, installed my 2 supplemental grounds outside, there's an existing ground rod below the panel which I will bring a #4 copper wire. My question is this. All the copper piping and water meter in the house is feed by a piece of plastic piping coming out from the basement floor from the street. Do I need to bring a wire from the panel to ground the copper piping ? If so what size? The meter is 30 feet away, the copper piping comes over to the water heater where the panel is , can I ground there? Thank you
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
if you have plastic coming in from outside and copper throughout the house then run a #4 to the water pipes at the closest location.

btw #6 is all you need for the ground rods
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Since you do not have a water pipe electrode you do not need to connect a GEC to the water pipe, however as Dennis has stated the metallic interior water piping system is required to be bonded. That bonding requirement is in 250.104(A) using table 250.102(C)(1) at any convenient point on the water piping system.
 

Eagle126

Member
Perfect exactly what I was looking for. I did run #4 copper from my meter to the 2 ground rods per 250.66, you said I could use #6, did I use the wrong table? Where is that in the code, thank you
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Perfect exactly what I was looking for. I did run #4 copper from my meter to the 2 ground rods per 250.66, you said I could use #6, did I use the wrong table? Where is that in the code, thank you

Forget the table, read the whole article.

Roger
 

Eagle126

Member
Forget the table, read the whole article.

Roger

I read the complete article and know realize that a #6 copper wire was all that was required. Know I understand that I need to ground the water piping system that has the plastic coming in feeding the water meter, since it's not a true grounding electrode can I also install a #6, I see you mentioned #4, can you explain, thank you
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I understand that I need to ground the water piping system that has the plastic coming in feeding the water meter,

See 250.104 for specifics of bonding the water piping.

Roger
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I read the complete article and know realize that a #6 copper wire was all that was required. Know I understand that I need to ground the water piping system that has the plastic coming in feeding the water meter, since it's not a true grounding electrode can I also install a #6, I see you mentioned #4, can you explain, thank you

Table 250.66 tells you what size conductor to use for a grounding electrode. Normally that would be needed for all electrodes but there are some exception. One of the exception is that a #6 is all that is needed to the ground rod.

If the water line is an electrode then T250.66 comes into play and usually that is a #4 for a 200 amp service but the size of the grounding electrode conductor is based on the size of the service conductors.

If the water line is not an electrode and there is copper throughout the house then the copper line need to be bonded based on T250.102(C)(1) which is very close to the same as T 250.66-- thus a #4 would be needed in most cases for a 200 amp service
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
you can use #6 copper to ground rods for any size service.
My reference to 250.104 is not pertaining to grounding, the OP has clarified that the water pipe does not meet the criteria of being an electrode so it only needs to be bonded which could be accomplished with the EGC of a branch circuit.

I think the OP knows a #6 is all that is needed for a rod after he read 250.66

Roger
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
My reference to 250.104 is not pertaining to grounding, the OP has clarified that the water pipe does not meet the criteria of being an electrode so it only needs to be bonded which could be accomplished with the EGC of a branch circuit.

No minimum size?
 

kwired

Electron manager
Location
NE Nebraska
No minimum size?

Unless it has changed over the years, it must be size of the GEC to the interior metal piping system. Had to change that once when GEC would have needed to be more than 6 AWG even though the only electrode I had on that one was a CEE with the max required 4 AWG run to it.

My understanding for 6 to rods (and pipe electrodes) and 4 to CEE's is that those electrodes have been determined to not be able to dissipate any more energy than the respective max size conductor can deliver to them so there is no point in running larger conductors to them. Surprising copper industry people haven't done studies to prove this otherwise:blink:
 