    Hospital grade

    Can non hospital grade receptacles be installed in other than patient care areas?

    #2
    Yes, and as a matter of fact, hospital grade receptacles are not required in many patient care areas

    Roger
    Moderator

    Comment


      #3
      Originally posted by roger View Post
      Yes, and as a matter of fact, hospital grade receptacles are not required in many patient care areas

      Roger
      Thanks Roger, I can't seem to find out exactly where they are required. Any help would be much appreciated.

      Comment


        #4
        Originally posted by mortimer View Post

        Thanks Roger, I can't seem to find out exactly where they are required. Any help would be much appreciated.
        Generally they are required at patient bed locations. Look at 517.18(B), 517.19(B)(2), and 517.19(C)(2). Some cord an plug medical equipment may also be required to be plugged into a hospital grade receptacle per the manufacturer's instructions.

        Comment


          #5
          There is also 517.61(C)(2)

          Roger