Spare conduit stub-up into hazardous space. Seal fitting required?

Status
Not open for further replies.

lakee911

Senior Member
Location
Columbus, OH
Let's suppose that I stub up a spare conduit into a hazardous space. Would I be required to install a seal fitting or if I cap it at the first joint, would this be code compliant?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Is it connected to a box? Then there is little wiggle room based on 501.15 (if this is a class 1 installation).

If it is not connected to a box than maybe it is not a piece of conduit and as long as there was no way for hazardous vapors to get from the classified space to an unclassified areas, maybe there is some wiggle room.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
If there are no conductors, the raceway is only a hole in the ground and can simply be capped off. Once it becomes part of a wiring method other considerations come into play. "Grade" is always a boundary so either Section 501.15(A)(4) or 501.15(B)(2) must be addressed.

BTW Hazardous Location questions will usually receive better attention in the Hazardous (Classified) Locations Forum.
 