    Poll for Inspectors

    Section 680.74, 2005 NEC.
    Here's the situation.... Jetted whirlpool tub, residential wood frame construction, PEX (plastic) water line from a manifold in basement near the incoming 3/4" copper water main from the street. do you require..........
    a) a # 8 copper bond wire from the metal motor frame to the hot/cold faucet assemblies on the tub
    or...........
    b) a # 8 copper bond wire run to the incoming water main approx 100' away from the tub
    or..........
    c) some other option that I have not listed

    I know how I would (and have) done this, how would this be enforced in your areas?
    Thanks,
    Jim

    #2
    I wouldn't require anything...there is not a metal water piping system.
    Ryan Jackson, Salt Lake City
    Inspector, Instructor

    Comment


      #3
      If it's all plastic pipe I wouldn't worry about it, that is if we're talking about a bathtub type whirlpool.

      Mine is fiberglass, all of the piping is plastic and the motor is the plastic case type that doesn't require bonding and the water pipe is already bonded.
      I can build anything you want if you draw a picture of it on the back of a big enough check.

      [COLOR=red]There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one.[/COLOR]

      John Childress
      Electrical Inspector
      IAEI / CEI / C10
      Certified Electrical Inspector

      Comment


        #4
        c) Other option

        My "option" ~ nothing.

        Comment


          #5
          I agree with Ryan and John,

          If there is no metal piping system, then there is nothing to bond.

          680.74 requires all metal piping systems and all grounded metal parts in contact with the circulating water to be bonded together.

          Comment


            #6
            nothing here, either

            Comment


              #7
              No bond required.
              Ron

              Comment


                #8
                I too agree with all the above comments...
                Bryan P. Holland, MCP
                NEMA - Codes & Standards

                Comment


                  #9
                  680.74

                  Hi: To answer the particulars of your poll... IMO, the idea of 680.74 is to establish an equipotential plane around the tub similar to swimming pool bonding grids and agricultural equipotential planes. The equipment grounding conductor of the pump motor takes care of ground-fault currents. No need to extend bonding conductor to panelboard or service equipment.
                  [COLOR=seagreen]Answers based on the 2008 NEC Edition when I think to grab that one.[/COLOR]

                  [COLOR=darkorchid]What you are, you are by accident of birth; what I am, I am by myself. There are and will be a thousand princes; there is only one Beethoven. [/COLOR]


                  Comment


                    #10
                    I agree with others. Nothing required IMHO.

                    Pete
                    Experience is something thats gained shortly after you really needed it.

                    Comment


                      #11
                      Add me to the list. No bonding required.
                      Rob

                      Moderator

                      All responses based on the 2017 NEC unless otherwise noted

                      Comment


                        #12
                        I wonder how many pages this can go with everyone agreeing?

                        Comment


                          #13
                          Originally posted by Jljohnson
                          I know how I would (and have) done this,
                          Would you let us know how you would (and have) done this?
                          Mike Whitt
                          [COLOR=#000066]God answers Knee-Mail. [/COLOR]

                          Comment


                            #14
                            No further action required for this situation.


                            Oops this was a poll for inspectors.
                            [COLOR="Navy"]There are two kinds of people - those smart enough to know they donít know, and those dumb enough to insist they do[/COLOR].-----Margery Eagan

                            [COLOR="DarkRed"]Open shop since 1988[/COLOR]

                            Comment


                              #15
                              ditto - no bonding