I need to install gen purpose 20 amp receptales 115' to 145'. to adjust for voltage drop, I will need to run #8 cu. is it acceptacle to pig tail # 12 at the J box to attach the receptacle?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I need to install gen purpose 20 amp receptales 115' to 145'. to adjust for voltage drop, I will need to run #8 cu. is it acceptacle to pig tail # 12 at the J box to attach the receptacle?
Yes, as long as your OCPD is not more than 20a.
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
Do you have a known load that your trying to carry ? That is not a distance that usually requires #8 ,maybe #10 ,a 5 volt drop from panel usually is no problem
 

iwire

Moderator
Staff member
Location
Massachusetts
We generally run 12 AWG out to 100' radius from the panel and 10 AWG out to a 200' radius. It is really imposable to determine what size is really needed. You would need to know the load and how tolerant the load is to voltage drop.
 