I need to install gen purpose 20 amp receptales 115' to 145'. to adjust for voltage drop, I will need to run #8 cu. is it acceptacle to pig tail # 12 at the J box to attach the receptacle?
Yes, as long as your OCPD is not more than 20a.I need to install gen purpose 20 amp receptales 115' to 145'. to adjust for voltage drop, I will need to run #8 cu. is it acceptacle to pig tail # 12 at the J box to attach the receptacle?