Question Pertaining to Single Family Dwelling Hot Tub Installation. Feeders and Branch circuits.
A proper size breaker (60A) installed in the 40 circuit main breaker panel, the breaker is connected to a 6/3 WG NMB cable. The cable is runned to a two circuit main lug load center with a double pole 50A GFCI circuit breaker. The breaker serves as both the disconnect switch and provides the GFCI protection for the Hot Tub. The wiring method on the load side of the GFCI to the Hot Tub is liquid-tight with an insulated Equipment Ground Conductor.
Is this a code compliant installation?
Reference: 680.25, 680.25(a), 680.42(c)
A proper size breaker (60A) installed in the 40 circuit main breaker panel, the breaker is connected to a 6/3 WG NMB cable. The cable is runned to a two circuit main lug load center with a double pole 50A GFCI circuit breaker. The breaker serves as both the disconnect switch and provides the GFCI protection for the Hot Tub. The wiring method on the load side of the GFCI to the Hot Tub is liquid-tight with an insulated Equipment Ground Conductor.