Ground Ring Question

Status
Not open for further replies.

bvano1983

Member
Location
El Paso, TX
250.52(A)(4) uses the word "encircling" does that mean the ring HAS to "encircle" the building or just has to have 20ft of an attempt to go around the building.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
While there is no technical reason why the ground ring has to encircle a building or structure, that is what the code requires. 20' of #4 copper run in a straight line would be just as effective, if not more effective, than that same 20' of #4 run in a circle.
 