Ground Screws

Status
Not open for further replies.

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
... I don't think the NEC really covers the bonding of the cover. ...
I may just be misinterpreting your point (it happens all the time with my creeping senility), but I believe 250.4(A)(3) and 250(B)(2) apply here. They may not specifiy the means, but they do lay the "ground work" for general requirements.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I may just be misinterpreting your point (it happens all the time with my creeping senility), but I believe 250.4(A)(3) and 250(B)(2) apply here. They may not specifiy the means, but they do lay the "ground work" for general requirements.
Bob,
I agree that the metal parts of electrical equipment have to be bonded, but as you say the code does not really address the issue. Does the rule in 250.134 apply? I think not. I think that the issue is or should be covered by the product standards and not the NEC.
 