Is a GFCI protected receptacle required for an ice machine? If so, where can I find this in the Code?
Thanks for all replies.
Thanks for all replies.
Is a GFCI protected receptacle required for an ice machine? If so, where can I find this in the Code?
Thanks for all replies.
Meant to add this is not a dwelling unit...
Nothing in 210.8(B) says 'ice machines' it lists locations.
So if that ice machine is 15 or 20 amps 125 volts, connected via a cord & plug, located in a commercial kitchen (or any of the other listed locations) it must be GFCI protected
It is in an alcove in a Cafe in the new Boeing plant here in North Charleston. I agree that GFCI is needed after re-reading 210.8(B). Plus the AHJ wants it which over rides any interpretation of the Code.
Thanks for all your replies.
Is it written in black & white what the AHJ requires ? When nothing is in writing,
it becomes the AHJ's opinion which he just pulled out of his ... Tell the AHJ to
pound sand.