Feeder Grounded Conductor Minimum Size

Status
Not open for further replies.

beanland

Senior Member
Location
Vancouver, WA
2011 NEC 215.2(A)(2) appears to refer to itself. "Additional minimum sizes shall be as specified in 215.2(A)(2)..."

Can anyone explain that reference?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
215.2(A)(2) is pretty clear. The grounded conductor (neutral) shall not be smaller than the egc from T. 250.122. Thus a 100 amp feeder would need a neutral sized at #8. Remember if the feeder doesn't require a neutral then one is not required. If you decide to pull one for future use then it cannot be smaller than the egc, as Walker stated above.
 