What is the max that you can backfed a mian lug only panel that has a 800 amp bus rating i have conflicting numbers. I think its 160 amp and the solar installer wants to install a 400 amp breaker.
This has no main it is a main lug only panel 500mcm from utility
Do you go buy the bus rating of the panel because there is no main?
How about the bus rating its 800 amp would there be a problem overloading the buss?
No. The solar is not a load, and cannot add any more current to the busbar than the load breakers already allow. If the current configuration is safe, it will also be safe with the solar.
Another consideration that I didn't see mentioned (only skimmed through post) was allowable breaker size by manuafacturer listing. Has to do with the breaker stab capacity. 400A breaker in an 800A panel probably isn't prohibited, but you need to check panel label or documentation to be certain.Thanks
If this was directed at me, the PV system breaker will be installed in a load position and backfed. Manufacturers restrict the sizes that can be used in the load positions. You need to verify a 400A breaker is permitted to be used in whatever position it will be located.The panel is protected from the high fuses on the utility side no breaker feeding this main lug only panel
I think it might have been directed at me, in response to my speculation on where, if anywhere, the OCPD was feeding the MLO panel.If this was directed at me, the PV system breaker will be installed in a load position and backfed. Manufacturers restrict the sizes that can be used in the load positions. You need to verify a 400A breaker is permitted to be used in whatever position it will be located.
I've had this argument before... 705.12(D)(2) does not kick in until you get to "distribution equipment" [see 705.12(D) general statement]. The AC combiner panel and its feeders are not distribution equipment... they are supply equipment as long as the serve no loads via the other source(s) of power.What if I have a 250A MLO AC combiner panel fed from a 125A breaker in the main switchgear? (3-phase, 3-wire) The feeders from the 125A breaker are #1 AWG THWN-2 CU. It seems like the limiting factor would be the conductors and not the bus of the panel. Therefore, the feeders can carry 150A which limits the total disconnect amperage to 150A x 120% = 180A. Section 705.12D of the 2011 NEC does not limit the 120% rule to just bus but also conductors.
This is one of the conundrums of multi-source supply systems. In short the reality of it is, if you do have a short in the feeder, there is no longer any reason to protect the conductors. It then becomes a personel and equipment protection issue.Another question raised to me by one of our more senior engineers is what is protecting the feeders when a MLO AC combiner panel is used? For example, I have 5 inverters feeding an AC combiner panel. The AC combiner panel is 250A MLO. Each inverter feed has a 45A breaker. The circuit breaker in the switchgear feeding the AC combiner panel is 225A and the wiring from the switchgear to the AC combiner panel is 4/0. Say there was a short in the AC wiring between the Switchgear and the AC combiner. What is protecting that feeder? Is each individual 45A breaker enough protection? I get the feeling that all AC combiner panels need to have a main at the panel although I know it's commonly done otherwise.
Another question raised to me by one of our more senior engineers is what is protecting the feeders when a MLO AC combiner panel is used? For example, I have 5 inverters feeding an AC combiner panel. The AC combiner panel is 250A MLO. Each inverter feed has a 45A breaker. The circuit breaker in the switchgear feeding the AC combiner panel is 225A and the wiring from the switchgear to the AC combiner panel is 4/0. Say there was a short in the AC wiring between the Switchgear and the AC combiner. What is protecting that feeder? Is each individual 45A breaker enough protection? I get the feeling that all AC combiner panels need to have a main at the panel although I know it's commonly done otherwise.