ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Electrical Engineer - Photovoltaic Systems
We sent our master electrician and a helper out to a site where we had a PV system installed by a contractor (who is long gone, of course) a couple of years ago to investigate why the system wasn't running. They determined that the problem had to be in the 150' underground DC run from the array combiner to the inverter. Our master stood next to the inverter and had the helper close the DC disco at the array, and he began to hear a sound like frying bacon emanating from the conduit. They pulled the wire and found that the contractor had somehow managed to slit the insulation on both the DC+ and DC- conductors. Apparently when the contractor meggered the run they found something wrong, pulled the wire, found the compromised insulation, taped it up, and pulled the wire back into the conduit, with predictable results over time when water got into the conduit. Both conductors were badly burned; the DC- only had 2 or 3 strands left.
Since it was a + to - fault and the insulation on the EGC was intact, the GFI on the inverter never saw it.
Since it was a + to - fault and the insulation on the EGC was intact, the GFI on the inverter never saw it.