Which makes absolutely no sense to me. If there is no main breaker on a panel connected to the service via a line side tap, there is no limit, other than the size of the service, to the current that can be supplied to the bus by the service.InnerS.,
Also, do you realize what the point of the 4 main breakers is, w/o a single main breaker?
The 120% rule will not apply here to the Buss - under any interpretation of the code, unless you have a buss fed from both ends ( e.g main breaker and pv breaker(s) ) . With 4 pv breakers all as main breakers there is no current that needs to be added going both ways, ie. no 120% rule to apply.
If we limit the available current from the service with a main breaker, then by the 120% rule the bus has to be rated to carry the main breaker current plus the inverter current divided by 1.2, but if there is no main breaker it only has to be sized to carry the inverter current divided by 1.2? Does that make any sense? Am I missing something?
Most of the code is written with only the current flowing from the service out to loads in mind; sometimes you have to stand on your head to interpret how it pertains to current flowing the other way.