Hello all,
I have a question about both Code and Physics as it relates to bonding of metal conduit used on the DC side of a solar system.
While the code is clear that any ferrous piping containing the Grounding Electrode Conductor needs to be bonded to the GEC at both ends 250.64(E) / 250.92 (B)(2)-(4), i don't find any similar requirement for the DC piping (which contains solar circuit conductors and an equipment ground but no GEC).
We have generally made it a practice to ground both ends of our DC EMT runs even though it does not appear to be a requirement of the NEC, based on the assumption that lightning induced induction is also possible on that section of pipe and inductive choking would be an issue there as well.
Is our practice overkill? Can anyone explain to me why there is no requirement for bonding metal conduit on the DC side of the solar system? Are those conductors less likely to have a lightning related surge in them that might be affected by inductive choking?
Thanks in advance for your thoughts and insight
~Fortunat
www.revisionenergy.com
I have a question about both Code and Physics as it relates to bonding of metal conduit used on the DC side of a solar system.
While the code is clear that any ferrous piping containing the Grounding Electrode Conductor needs to be bonded to the GEC at both ends 250.64(E) / 250.92 (B)(2)-(4), i don't find any similar requirement for the DC piping (which contains solar circuit conductors and an equipment ground but no GEC).
We have generally made it a practice to ground both ends of our DC EMT runs even though it does not appear to be a requirement of the NEC, based on the assumption that lightning induced induction is also possible on that section of pipe and inductive choking would be an issue there as well.
Is our practice overkill? Can anyone explain to me why there is no requirement for bonding metal conduit on the DC side of the solar system? Are those conductors less likely to have a lightning related surge in them that might be affected by inductive choking?
Thanks in advance for your thoughts and insight
~Fortunat
www.revisionenergy.com