Additional Array Grounding NEC 2014 690.47 D

Status
Not open for further replies.

SunFish

NABCEP Certified
Location
ID
Occupation
Sr. PV Systems Design Engineer
Can the additional array grounding electrode conductor required by 690.47 (D) in the 2014 NEC be run into a building, such as routing it through an attic space, before it lands on the grounding electrode or is there a code requirement that says this must be run external on buildings/dwellings?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
As far as I know there is no such code requirement. If the GEC is connecting an array on the roof to ground in only one place , I can't see what difference it would make and I would say it should be allowed.

However, if it is coming from a ground mount I believe it would be a terrible, terrible idea in lighting prone areas. Also if it acts as a bonding jumper between electrodes on opposite sides of the house I believe it would be a terrible, terrible idea. (IOW, don't put your 690.47(D) electrode on one side of the house and then put the DC conduit and inverter, connected to the AC GES, on the other side.)

Why do I think this? See this video from the host of this forum:
http://www.youtube.com/watch?v=YuDqXFvRv94

Ask your AHJ to watch it too.

In my opinion, 690.47(D) is itself a terrible idea.
 