And if the system uses a grid tie inverter (GTI) you will not have any batteries at all.
For off-grid battery systems the highest common voltage is 48V nominal, which could be twenty-four 2V batteries in series.
Voltages above 48VDC usually involve factory configured battery packs.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
And if the system uses a grid tie inverter (GTI) you will not have any batteries at all.
For off-grid battery systems the highest common voltage is 48V nominal, which could be twenty-four 2V batteries in series.
Voltages above 48VDC usually involve factory configured battery packs.
Also, once you get higher than 50V, the rules change.
 