Hi
I have a 120/240v open delta service with 1-50kw trans and one 10kw trans. The power co will let us connect 50kw single phase into the 50kw transformer. To meet 705.42 do I have to put in a phase loss relay and a contactor or since the inverters are single phase and not connected to all phases do I not have to do anything? I was going to use a phase loss relay to open the DC combiner box contactors but it looks like it would not meet code anyway because it says to open all ungrounded conductors. Any ideas?
Thanks
I have a 120/240v open delta service with 1-50kw trans and one 10kw trans. The power co will let us connect 50kw single phase into the 50kw transformer. To meet 705.42 do I have to put in a phase loss relay and a contactor or since the inverters are single phase and not connected to all phases do I not have to do anything? I was going to use a phase loss relay to open the DC combiner box contactors but it looks like it would not meet code anyway because it says to open all ungrounded conductors. Any ideas?
Thanks