Seprate structure

Status
Not open for further replies.

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
690.47(D) says yes, but it exists in the 2008 and 2014 codes, but not the 2011 code.

If there is more than one micro-inverter branch circuit on the structure, then 250.32 says yes, you need an electrode.

If the mounting structure meets the requirements of 250.52(A)(2) - one structural member in contact with the earth for 10ft or more - then you can use that and not install a rod.
 

Smart $

Esteemed Member
Location
Ohio
Under recent Code editions, if a grounding electrode system (GES) is required and you use one ground rod as an electrode to establish that GES, a second ground rod would be required unless you prove that one has 25 ohms or less resistance to earth using a standard electrode resistance measurement means.
 