ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Electrical Engineer - Photovoltaic Systems
I have a client who submitted and got approved a design for a commercial PV system which was to be interconnected through a 100A fused disco via a line side tap to the facility's 100A MDP. During construction they changed the design; they upgraded the panel to a 200A panel and downgraded the main breaker to 100A so that they could interconnect through a 100A backfed breaker in the MDP and get under the 120% rule for the panel. It looks like a safer design to me, since under the changed design there are no conductors unprotected by OCPD and the resultant current in the feeder to the MDP is unchanged.
The inspector failed the installation, saying that when they upgraded the panel they should have also upgraded the feeder to 200A conductors even though the main breaker is still 100A and the only thing that changed is the rating of the busbars. Is there code that stipulates this?
The inspector failed the installation, saying that when they upgraded the panel they should have also upgraded the feeder to 200A conductors even though the main breaker is still 100A and the only thing that changed is the rating of the busbars. Is there code that stipulates this?