I'm designing a system using Enphase microinverters of various string sizes feeding a subpanel. The 208V 3ph amperage output is relatively small, between 4A and 10A based on 6 and 15 per branch circuit. The mfr recommends using 20A breakers for the subpanel. If I have five 20A breakers in the sub, but the circuit amperages total only 36A, what size should the PV subpanel breaker be on the main switchboard? Do I just take 36A x 125% and round up to 50A? I don't think adding up the 20A breakers (100A) is the way to go. Is there a limit to how large a breaker it can be?
I can't find this discussed in the NEC for PV book. Please help.
Thanks!
I'm designing a system using Enphase microinverters of various string sizes feeding a subpanel. The 208V 3ph amperage output is relatively small, between 4A and 10A based on 6 and 15 per branch circuit. The mfr recommends using 20A breakers for the subpanel. If I have five 20A breakers in the sub, but the circuit amperages total only 36A, what size should the PV subpanel breaker be on the main switchboard? Do I just take 36A x 125% and round up to 50A? I don't think adding up the 20A breakers (100A) is the way to go. Is there a limit to how large a breaker it can be?