=electrofelon;1700584
1 I am confused. Are you discussing that 1000 amp service I mentioned previously?
2 I did a load calc and got 324200 VA (do you remember that: convert everything to VA?).
3 So finally, the utility hooks me up and I have no idea what size transformer they are using - I dont care or need to know.
Ill even do a quick recap:
1. No using X amps of Y volts. convert everything to VA.
2. The utility transformer and its size has nothing to do with us.
Homework: Considering #1 and 2 above, if I have a 1000 amp 120/208 three phase service, how many 120V, 1500 watt electric heaters can I use assuming they are balanced equally across the system and they are all on for 1 hour, then all off for 1 hour
1. Yes
2. 324.2kVA load calc meaning...all the equipment turned on at once? We're still talking about a 150kVA xfmr?
3. That's fine- there's no way for me to know either.
These below are the only options for 208/120 3 phase service from the POCO here. 3 pole mounted or single pad mounted 3 phase setups. The (( XXX )) is what you request when you want new service. You have to fill out the load sheet for the POCO of course.
I will guess however if i had your 324kVA load example, and it was "continuous", I'd have 1000A service, and a 500kVA xfmr setup.
If it was 324kVA for less than 30 minutes every once and a while and ½ of 324kVA (or 162kVA) 90% of the time, I'd have the 400A / 150kVA xfmr setup/service.
Options:
3-25kVA or 1-75kVA (( 200A ))
3-50 ..... or 1-150 (( 400A ))
3-75 or ...(no 225kVA pad mounted option- 3-75kVA pole only) (( 600A ))
3-100..... or 1-300 (( 800A ))
3-167..... or 1-500 (( 1000A ))
Well that homework leaves me in a bind.
I simply can't convert the 1000A to VA without...using the number for volts.
I also can't say that a 120V 1500w heater = load of 12.5 amps.
If I could, the answer would be 80 heaters.
80 heaters * 1500VA each = 120,000VA divided by 120V = 1000A.
I'd get (( 200A/75kVA )) or (( 400A/150kVA )) service at 208/120V 3ph for those 120kVA of heaters if they were the only load, depending of course on how often they ran.
Or I'd get 277V heaters and get (( 200A /150kVA )) of 480/277V (smallest standard option) to save on the electric bill. Or even 100A of 480/277V service (75kVA of xfmrs) if the heaters didn't run all at once.