david
Senior Member
- Location
- Pennsylvania
The micro string circuits should be combined at the detached garage and then run a feeder back to your AC combiner at the house. I would look to 225.30(A)(5) for allowing the additional feeder to the garage, (assuming it already has a power to the garage). Also follow 225.31, 225.32, 225.33, 225.34...and also label the 225.31 disconnect as the 690.12 Rapid Shutdown for the PV system on the detached garage. Then you need a grounding electrode system.
Transfer equipment? Why? The interconnection is just a simple load side connection through a breaker in the MDP like we build every day; it's just that the PV is on one building and the interconnection is on the other. The conductors from the PV do not interact with whatever power the garage has except that they are both tied to the same service.
I may not have stated it very well, but my comment wasn't directed at your PV array at the garage. i do not think the PV array falls under the scope of article 705 for the garage at all. Your system does not enter the garage. Do you agree that article 690 applies to the garage array. and Article 705 applies to the interconnection at the dwelling?
The micro string circuits should be combined at the detached garage and then run a feeder back to your AC combiner at the house.
My thought was that would be one way of doing it based on article 690
I would look to 225.30(A)(5) for allowing the additional feeder to the garage, (assuming it already has a power to the garage).
225.30 Number of Supplies.
(4) Optional standby systems
(5) Parallel power production systems
My though was if your feeder is not supplying in Parallel with the primary source feeder at the garage how does 225.30 (A) (5) provide a permissive path for a second feeder to a garage?
However 225.30 (4) a permissive rule would imply a transfer switch.
Article 690 would also provide allowance for a PV system Source supplying a garage but that would not be a feeder from a primary source correct?