I am trying to determine the required ampacity of a feeder tap conductor for a load side tap (assuming it is allowed by AHJ) to interconnect a 4200W (22A max current) to an existing service conductor directly downstream from a 100A main breaker. (service conductor ampacity unknown). I am seeing this done in the field and local AHJs are allowing for system POC/commissioning. I am trying to assess if it is acceptable based on a thorough look at NEC 705.12(D)(2)(2). When installers are doing this they are illustrating in design plans a line side tap incorrectly, and minimum wire size is often a #8.
My interpretation after looking at 705.12(D)(2)(2) and 240.21(B)(2) leaves me to believe that the ampacity of the conductors running from the load side feeder tap to the 25A fuses in the PV disconnect (assuming a length of not over 25 feet) must be #2AWG: 100A + (22A x .33) = 108A minimum ampacity (#2AWG)
Can anyone confirm or give me a professional opinion? Is the #8 Ok as long as the existing service conductors can handle 100A +22A PV? Or are the #8 conductors (minimum allowed ampacity for supply side interconnection) in danger? Is #2 AWG correct?
My interpretation after looking at 705.12(D)(2)(2) and 240.21(B)(2) leaves me to believe that the ampacity of the conductors running from the load side feeder tap to the 25A fuses in the PV disconnect (assuming a length of not over 25 feet) must be #2AWG: 100A + (22A x .33) = 108A minimum ampacity (#2AWG)
Can anyone confirm or give me a professional opinion? Is the #8 Ok as long as the existing service conductors can handle 100A +22A PV? Or are the #8 conductors (minimum allowed ampacity for supply side interconnection) in danger? Is #2 AWG correct?