705.12(C) Greater than 100 kW VS 705.12(D)(1) Dedicated Overcurrent and Disconnect
I am designing a 144 kW system with five 30 kW utility interactive inverters, batteries, transfer switches, micro-grid controllers, etc. It is a complex system and without getting into nitty gritty details, and there are lot of them, I was wondering if I could propose this question: Is it possible to have one inverter make a Load Side connection into a panelboard, say on the third floor, and to have the other four inverters make a load side connection into a panelboard, say on the first floor? The first floor inverters tie into four OCPDs at a "MLO PV Load Center" which then goes to a single PV breaker at the Main Panel.
What is the forums experience on this subject?
Thanks,
Michael
Side Question: If an inverter is rated 44 amps maximum AC current, and but the inverter company specifies a 50 Amp continuous operation rated breaker, am I allowed to design for this current or do I design OCPD and conductors for 125 percent of max current (55 Amps, next size up being 60 Amp breaker)?
705.12(C) Greater than 100 kW VS 705.12(D)(1) Dedicated Overcurrent and Disconnect
I am designing a 144 kW system with five 30 kW utility interactive inverters, batteries, transfer switches, micro-grid controllers, etc. It is a complex system and without getting into nitty gritty details, and there are lot of them, I was wondering if I could propose this question: Is it possible to have one inverter make a Load Side connection into a panelboard, say on the third floor, and to have the other four inverters make a load side connection into a panelboard, say on the first floor? The first floor inverters tie into four OCPDs at a "MLO PV Load Center" which then goes to a single PV breaker at the Main Panel.
What is the forums experience on this subject?
Thanks,
Michael
Side Question: If an inverter is rated 44 amps maximum AC current, and but the inverter company specifies a 50 Amp continuous operation rated breaker, am I allowed to design for this current or do I design OCPD and conductors for 125 percent of max current (55 Amps, next size up being 60 Amp breaker)?