# 6 PV bonding wire

Status
Not open for further replies.

Eros

Member
Location
United States
Does the #6 bare bonding wire that is installed on the PV array have to be continued to the inverter or can it be reduced in size when leaving the combiner box ? Code article ?
thank you
 

ryangittens

Member
Location
usa
The #6 bare is just for conductor protection (since #6 is the smallest wire that doesn't need any). A smaller wire can be used if it's protected.

So to answer your question, yes it can be reduced at the combiner. Can't remember the reference off the top of my head.

Sent from my SM-G950U using Tapatalk
 